Installation manual
Diagnostics and troubleshooting
S1A53838 09/2011 153
Alarm Conditions
Alarms do not cause the drive to enter a fault condition.
Alarm Codes
Code Description Possible causes Remedies
Atn1
[
Auto tune]
• Auto-tuning in process • Normal if it the message disappears 
after a few seconds.
CLr
[
Reset active]
• This message is displayed after the 
STOP key is pressed while an detected 
fault is displayed.
• Press the STOP key again to clear the 
detected fault.
db
[
DC braking]
• DC braking in process • The alarm code goes off in several 
seconds if no trouble occurs.
dbOn
[
dbOn]
• Motor shaft fixing control • 
E-17
[
HMI error]
• A graphic display option key has been 
held down for more than 20 seconds.
• A graphic display option key may not be 
operating properly.
• Release the graphic display option 
key.
• If this does not clear the error, replace 
the drive.
EI
[Excess value] 
The number 
of digits that can be 
displayed has been 
exceeded
• The number of digits entered for values 
such as frequencies is more than 4 (the 
upper digits have priority).
• Lower the frequency free-unit 
magnification [Customized freq val] 
(F702).
EOFF
[
Loc. Stop en.]
• The operation panel is used to stop the 
operation in automatic control or remote 
control mode.
• Press the STOP key for an emergency 
stop. To cancel the emergency stop, 
press any other key.
Err1
[
Speed ref alarm]
• The frequency setting signals at points 1 
and 2 are set too close to each other.
• Set the frequency setting signals at 
points 1 and 2 apart from each other.
h999
[Pin&1MWh] 
Integral input 
power
• Integral input power is more than 
999.99 kWh. 
• Press and hold down the ENT key for 
3 s or more when power is off or when 
the input terminal function CKWH is 
turned on or displayed.
H999
[Pout&1MWh] 
Integral 
output power
• Integral output power is more than 
999.99 kWh.
• Press and hold down the ENT key for 
3 s or more when power is off or when 
the input terminal function CKWH is 
turned on or displayed.
HEAd
End
[Head]
[End]
Display of first/last data 
items
• The first and last data item in the auh 
data group is displayed.
• Press MODE key to exit the data 
group.
H1
LO
[High]
[Low]
Parameter adjustment 
error
• During programming, a value was 
entered that exceeds the maximum or 
minimum value of the parameter.
• Enter a value within the bounds of the 
parameter
InIt
[
Initialization]
• Parameters are being initialized to 
default values.
• Normal if the message disappears 
after several seconds.
LStp
[Low speed stop] 
Auto-stop 
because of continuous 
operation at the lower-limit 
frequency
• The automatic stop function selected 
with F256 was activated.
• To deactivate the automatic stop 
function, increase the frequency 
command above the lower-limit 
frequency LL+F391 or turn off the 
operation command.
NOFF
[
Line undervolt flt]
• The phase-to-phase input voltage is too 
low.
• Measure the main circuit supply 
voltage. If the voltage is at a normal 
level, the drive requires repair. 
OFF [Drive stop]
• The ST-CC (run permissive) circuit is 
open.
• Close the ST-CC circuit.
nSt [Lock State]
• The Li is already active when the function 
is validated.
• The Li is already active when a 
configuration transfer is done with the 
function is validated.
• Deactivate the active Li configured.
rtrY
[
Auto reset]
• The drive is in the process of restart.
• A momentary stop occurred.
• The drive is operating normally if it 
restarts after several seconds.
StOp
[Stop supply] 
Momentary 
power loss slowdown stop 
prohibition function 
activated.
• The slowdown stop prohibition function 
set with F302 (momentary power loss 
ride-through operation) is activated.
• To restart operation, reset the drive or 
input an operation signal again.










