Troubleshooting guide
Table Of Contents

1336 PLUS II - 6.16 - September, 2001
Troubleshooting and Error Codes 3-5
Hertz Err Fault
29
This fault indicates that there is not 
a valid operating frequency. It can 
be caused by any of the following:
1. [Maximum Freq] is less than 
[Minimum Freq].
2. Skip frequencies and skip band-
width eliminate all operating 
frequencies.
3. Analog input signal speed
reference has been lost. See 
[Anlg Signal Loss] and
[4-20mA Loss Sel].
1. Check [Minimum Freq] and [Maxi-
mum Freq] parameters.
2. Check [Skip Freq 1], [Skip Freq 2], 
[Skip Freq 3] and [Skip Freq Band] 
parameters.
3. Check for broken wires, loose con-
nections or transducer loss at analog 
inputs.
Hertz Sel Fault
30
A frequency select parameter has 
been programmed with an out of 
range value.
Reprogram [Freq Select 1] and/or [Freq 
Select 2] with a correct value. If prob-
lem persists, replace Main Control 
Board or complete drive.
HIM -> Drive Refer to Table 3.B.
Ill Prog Input
62
[Fault Data] = 98 – “3 Wire” is 
selected as the [Input Mode] and 
one or more digital inputs are pro-
grammed to “Run Reverse” (2 wire 
action).
Reprogram the digital inputs or select 
“2 Wire” as the [Input Mode].
Input Phase Flt
49
The DC bus ripple has exceeded 
the value in [Phase Loss Level].
1. If the drive is operated on sin-
gle-phase, the load derating level 
has been exceeded.
2. Check incoming power for a missing 
phase/blown fuse.
Load Loss Flt
20
[Load Loss Detect] is set to 
“Enabled” and the drive output 
torque current was below [Load 
Loss Level] for a time period 
greater than [Load Loss time].
1. Verify connections between motor 
and load.
2. Verify level and time requirements or 
disable [Load Loss Detect].
Loop Overrn Flt
23
An overrun of the 2.5ms control 
loop has occurred.
Check all connections to the Main Con-
trol Board. Replace the board or com-
plete drive as needed.
Max Retries Fault
33
Drive unsuccessfully attempted to 
reset a fault and resume running 
for the programmed number of 
[Reset/Run Tries].
Check fault buffer for fault code requir-
ing reset. Correct the cause of the fault 
and manually clear by pressing the 
local Stop key or cycling the TB3 Stop 
input.
Motor Mode Flt
24
A fault has been detected originat-
ing from the Control Board. 
Check all connections to the Control 
Board. Replace the board or complete 
drive as required.
Motor Stall Fault
06
Current remained over [Current 
Limit] setting (parameter 36) for 
more than 4 seconds.
If the motor is drawing excessive cur-
rent (over [Current Limit] setting), the 
motor load is excessive and will not 
allow the drive to accelerate to set 
speed. A longer accel time or a 
reduced load may be required.
Motor Thermistor
15
An analog option board with ther-
mistor input is installed and the 
value at the terminals is less than 
60 ohms or greater than 3300 
ohms.
1. Verify that thermistor is connected.
2. Motor is overheated. Reduce load.
3. Thermistor is not present. Remove 
option board.
Name & Fault # Description Action










